Hi All
I am running DCE version 7.6 and try to define an alarm for temerature.
If I right click on the Netbotz 550 device there are no menu for creating an alark, that is only in
"Netbotz Appliance configuration", but then it will not show in DCE Alarm configuration.
Is there a way to configure alarms for the netbotz 550 so the will be visibel in Alarm configuration ?
Br Per
(CID:147198331)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by Per Christiansen on 2019-07-25
Hi Steve
Thanks for a fast reply.
Br Per
(CID:147198352)
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-07-25
Hi Per,
That's the way NetBotz and DCE have always worked together. NetBotz appliances alert for themselves based on their own thresholds. The following k-base provides a little more detail but basically, DCE can only be configured to alert for SNMP devices (including NetBotz 200 and 700 series) and modbus devices but not NetBotz 3xx, 4xx, and 5xx devices:
http://www.apc.com/us/en/faqs/FA355582
Thanks,
Steve
(CID:147198334)
This answer was originally posted on DCIM Support by Per Christiansen on 2019-07-25
Hi Steve
Thanks for a fast reply.
Br Per
(CID:147198352)