EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-04 01:36 AM
Hi team,
we have an issue with a customer that we cannot access to DCE with the Desktop Client neither Web Client. It seems that the server is not working properly, because in the web client we cannot enter user and passsword, we only see the top menu but a message that says that without connection to the server. With the desktop client we do not receive any response after inserting username and password.
We have rebooted the virtual machine and nothing changed. In the virtual machine console we can access with the apcsetup user and it seems that the configuration menu works.
Any other suggestion? Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-04 04:09 AM
Hi Shaun,
finally we restored a full virtual machine backup from yesterday and it is working again. We do not know what happened...
Thanks for your support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-04 04:05 AM
Hi @jzurera,
I'm struggling to picture the error you're giving - would it be possible to share a screenshot of what you see in the web?
Can we double-check you're using HTTPS? HTTP is not enabled by default any more.
Has the apcsetup configuration been completed? There's a new change in 7.8.0/7.8.1 that we don't have a default user anymore (eg apc/apc) in the web, so one of the last things apcsetup asks you is to create a DCE user - and the web service won't be running until this has been done.
Thanks,
Shaun
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-04 04:09 AM
Hi Shaun,
finally we restored a full virtual machine backup from yesterday and it is working again. We do not know what happened...
Thanks for your support.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.