DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

Highlighted

DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

This question was originally posted on DCIM Support by sheep on 2020-01-05


Hi, 

I want to update the Date & Time using SNMP Device Configuration,

However, I have a problem when I tried to configure few PDUs:

Under the column - Last Retrieved appears "Not Retrieved (in red color)"

Moreover, I have to do not mark in the hostname checkbox in order to

continue to Configure Device Settings.

What can I do to fix this?

Great appreciation

 

(CID:153551060)

8 REPLIES 8
Highlighted

Re: DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

This answer was originally posted on DCIM Support by Mate Fekete on 2020-01-06


Hi,

I'm just another user who had similar problem in the past. It was related to blocked firewall ports/protocols especially where DCE wants to send configuration to the device (21 or 22).

See more details here: 

StruxureWare Data Center Expert Security

(CID:153551172)

Highlighted

Re: DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

This comment was originally posted on DCIM Support by sheep on 2020-01-07


Hi friend,

 

Tank you for the help, but the problem is not blocked firewall and

I noticed that the problem appears on a specific model AP8853: 32A-1PH.

Do you have this model?

 

Great appreciation

 

(CID:153551800)

Highlighted

Re: DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

This comment was originally posted on DCIM Support by spezialist on 2020-01-07


Dear sheep,

Can you show a screenshot of the firmware version from the web-GUI of your problematic AP8853 rPDUs?

With respect.

(CID:153551879)

Highlighted

Re: DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

This comment was originally posted on DCIM Support by sheep on 2020-01-08


HI,

The firmware version:

Rack PDU: 6.5.6 

APC OS(AOS): 6.5.6

Boot Monitor: 6.5.6

With respect.

 

(CID:153552066)

Highlighted

Re: DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

This comment was originally posted on DCIM Support by spezialist on 2020-01-09


Dear sheep,

Maybe you should try updating one or two of the above rPDUs to the latest version v.6.8.2 and see the result?

Also, what is your version of DCE software?

With respect.

(CID:153552518)

Highlighted

Re: DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

This comment was originally posted on DCIM Support by sheep on 2020-01-09


HI,

The version of DCE software: 7.5.0.62

I will try update to v.6.8.2 can you please send my a link for download?

But I have a lot of other PDUs with this version 6.5.6 that work great without any problem.

Important notice: the problem that I have is with a specific

model AP8853: 32A-1PH.

Maybe the problem is with this controller version?

 

 

With respect.

(CID:153552538)

Highlighted

Re: DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

This comment was originally posted on DCIM Support by spezialist on 2020-01-10


Dear sheep,

Unfortunately, I could not find the web-links for the download ☹️. But you can download the latest DCE device firmware catalog, import it into DCE software, and from there update your problematic rPDUs.

I also have many rPDUs of AP8853 and AP8881, all with the latest firmware v.6.8.2. And I did not observe any problems on them.

Hope this helps you.

With respect.

(CID:153552743)

Highlighted