Where can I get log of who and when did users log in to Datacenter expert?
(CID:116920701)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:11 PM . Last Modified: 2 weeks ago
Hi ieslmarketing,
This information can by easy find in DCE Web-console under Event Log tab in Category Security, for example https://you_DCE_server/desktop/#eventlog&category=Security&relativeTimeDays=7 (or http://you_DCE_server/desktop/#eventlog&category=Security&relativeTimeDays=7).
You must have rights administrator of DCE server.
With best regards.
(CID:116920708)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:11 PM . Last Modified: 2 weeks ago
Hi ieslmarketing,
This information can by easy find in DCE Web-console under Event Log tab in Category Security, for example https://you_DCE_server/desktop/#eventlog&category=Security&relativeTimeDays=7 (or http://you_DCE_server/desktop/#eventlog&category=Security&relativeTimeDays=7).
You must have rights administrator of DCE server.
With best regards.
(CID:116920708)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:11 PM . Last Modified: 2 weeks ago
I logged out and logged back in but it shows blank still:
(CID:116920955)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:11 PM . Last Modified: 2 weeks ago
Hi ieslmarketing,
I suspect, that events are displayed after a while, for example, 24 hours, and not immediately. This needs to be checked...
With best regards.
(CID:116920966)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:11 PM . Last Modified: 2 weeks ago
Hi ieslmarketing,
Unfortunately, the user login/logout in the DCE Web-console is not journaled as events. Therefore, they are not displayed in what you are convinced.
But the user login/logout in the DCE-client is logged and can be seen in the Event Log tab.
At the same time, the DCE-server logs both events, all failed attempts to login to the DCE Web-console and the DCE-client. And also logged out due to error events.
With best regards.
(CID:116923309)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:12 PM . Last Modified: 2 weeks ago
Is the Event Tab located to the bottom right of the CLient? I am going through the options menu and I am not seeing anything labeled event logs.
Do advise.
(CID:116923304)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:12 PM . Last Modified: 2 weeks ago
ieslmarketing, Event Log tab in DCE Web-console, not in DCE-client:
With best regards.
(CID:116923306)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:12 PM . Last Modified: 2023-10-22 01:10 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.