This question was originally posted on DCIM Support by m.shahid on 2016-09-08
In DCE 7.2.0 Alert Configuration > due to electric In / Out, we got too many device communication lost emails. We setup 300 seconds (05 minutes) delay in Communication Status / Link Status using 'Return to Normal Delay' Setting.
This is in case of a device failure, DCE will check device status for 05 minutes if device discovery fails DCE will send email, Unfortunately it is not happening.
Your support is requested to overcome with the situation.
(CID:108824744)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:53 AM
This answer was originally posted on DCIM Support by Cory McDonald on 2016-09-12
(CID:108825190)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:53 AM
This comment was originally posted on DCIM Support by Ditte Drewer Mathiasen on 2016-09-12
Hi m.shahid, thanks for posting. Lets see who can be of assistance here. @community any ideas? Kind regards Ditte
(CID:108825044)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:53 AM
This answer was originally posted on DCIM Support by Valentin Kozlov on 2016-09-12
Hi Muhammad!
You need to change your settings. Return to Normal Delay is used when you need to be sure that alert condition is gone. In this case DCE wait 300 seconds and than send email if there is no alert conditions for the sensor.
For your case you should use another threshold type State For Time or State Mismatch For Time. Unfortunately there is no such settings for Communication Lost alerts, but you can workaround it with device state sensors which present on almost all devices.
You need:
Now, when device status changed from Normal to something else, DCE will send email after 5 minutes.
(CID:108825148)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:53 AM
This answer was originally posted on DCIM Support by Cory McDonald on 2016-09-12
(CID:108825190)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:54 AM
This comment was originally posted on DCIM Support by m.shahid on 2016-09-15
Implemented solution from Valentin Kozlov. Waiting for result. Thanks for support 🙂
(CID:108825534)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:54 AM . Last Modified: 2023-10-31 10:24 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.