  • Cyberpower UPS Sensors - Showing Unplugged
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49417members
Join Now
242718posts
Join Now

Cyberpower UPS Sensors - Showing Unplugged

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:53 PM
0 Likes
10
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:53 PM

Cyberpower UPS Sensors - Showing Unplugged

This question was originally posted on DCIM Support by Bruce Phillips on 2018-12-03


HI 

When I first discover this UPS (SNMP device)I have all the sensor values. See below image

After a few minutes. I assume after it is polled again they show as unplugged. see below.

 

Any explanation for this ?

I am assuming the poll is being rejected by the UPS somehow? If I delete this device in DCE and rediscover it nothing is discovered. I have to stop/start SNMP on the UPS and reboot the NMC (RMCARD202). It can now be discovered again in DCE. 

I am using CyberPower DDF file and other CyberPower UPS are ok.

 

I was suspecting faulty card however. I have tested using a CyberPower motioning software using the same snmp protocol and keys without issue to see if it can be discovered it works fine  and sensors have values all the time (Though u would expect there tool to be compatible)

I can SNMPwalk to it as well via DCE and tools ok.

 

Any suggestions?

cheers

Bruce

(CID:137106582)

Labels
  • Data Center Expert
  • DDF
Share
  • All forum topics
  • Previous Topic
  • Next Topic
10 Replies 10
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:53 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:53 PM

Re: Cyberpower UPS Sensors - Showing Unplugged

This comment was originally posted on DCIM Support by spezialist on 2018-12-09


Dear Bruce Phillips,

Tell us please, did you solve this problem or not?

With respect.

(CID:137109198)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:53 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:53 PM

Re: Cyberpower UPS Sensors - Showing Unplugged

This comment was originally posted on DCIM Support by Bruce Phillips on 2018-12-09


No not yet.  have just had a DDF created specific to this UPS so I will load that into DCE and rediscover device . Will try today and see how we go

(CID:137109456)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:53 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:53 PM

Re: Cyberpower UPS Sensors - Showing Unplugged

This comment was originally posted on DCIM Support by spezialist on 2018-12-10


Ok, I would be interested to know the result.

With respect.

(CID:137109520)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:53 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:53 PM

Re: Cyberpower UPS Sensors - Showing Unplugged

This comment was originally posted on DCIM Support by Bruce Phillips on 2018-12-12


There was no change. I installed new DDF in to DCE. Then rebooted card, stopped and started snmp on card. Rediscovered the device in DCE however sensors are still showing unplugged.

(CID:137110645)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:53 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:53 PM

Re: Cyberpower UPS Sensors - Showing Unplugged

This comment was originally posted on DCIM Support by spezialist on 2018-12-12


Dear Bruce Phillips,

That is, you wanted to say: first, your UPS is normally discovered in DCE software with all its sensors. And then after ~5 minutes, all your UPS sensors in DCE software go into Unplugged state. It's right?

What is the name of the DDF-file you use and what is its version?

With respect.

(CID:137110872)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:53 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:53 PM

Re: Cyberpower UPS Sensors - Showing Unplugged

This comment was originally posted on DCIM Support by Bruce Phillips on 2018-12-12


Hi there

Yes that is correct. 

DDF is cyberpower.xml Version 3

Other CyberPower devices are fine in DCE. Just this one. 

I am suspecting it must be faulty card.

 

cheers

Bruce

 

 

 

 

 

 

(CID:137111453)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:53 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:53 PM

Re: Cyberpower UPS Sensors - Showing Unplugged

This comment was originally posted on DCIM Support by spezialist on 2018-12-13


Dear Bruce Phillips,

From your comments:

Other CyberPower devices are fine in DCE. Just this one. 

I am suspecting it must be faulty card.

If all your UPS's you specified are the same series (the same model), and only with one you have such strange problems, then the problem is not in the DCE-server. It is very likely, that the problem is either in the NMC of this UPS, or on the network. In this case, of course, you better first ask the help of the vendor of this UPS.

Hope this helps you.

With respect.

(CID:137111639)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:54 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:54 PM

Re: Cyberpower UPS Sensors - Showing Unplugged

This comment was originally posted on DCIM Support by Bruce Phillips on 2018-12-13


Yep I agree. I am waiting on a replacement card. And will put that in when  I get a chance

(CID:137112221)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:54 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:54 PM

Re: Cyberpower UPS Sensors - Showing Unplugged

This comment was originally posted on DCIM Support by spezialist on 2018-12-14


Ok, in any case I would be interested to know the details.

With respect.

(CID:137112323)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:54 PM
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:54 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric