Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Cooling unit simulate impact
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51219members
Join Now
245431posts
Join Now

Cooling unit simulate impact

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Venkat
Ensign Venkat Ensign
Ensign
‎2020-07-24 02:10 AM
0 Likes
5
803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-24 02:10 AM

Cooling unit simulate impact

Hi,

 

One of our cusotmer having DCO -  v8.3.2 and we have simulated the Cooling Impact and 5 Cooling Units and found the same racks showing impact for all the Cooling units.  

 

If we change the power capacity to predicted power value in preference, there is no impact showing for the Cooling Units.

 

The screen shot attached for your kind reference.

 

Thanks - K.Venkat

 

 

 

 

 

Solved! Go to Solution.

Attachments
Labels
  • Data Center Operation
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
ATrabert
Lieutenant JG ATrabert Lieutenant JG
Lieutenant JG
‎2020-07-30 10:10 AM
0 Likes
0
741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-30 10:10 AM

Re: Cooling unit simulate impact

Hi Venkat,

Glad you're seeing more expected values, I should have been more specific but I was asking for estimated load of room (eg Floor PDU load) and the Cooling Capactiy of the cooling units. CFM would also be relevant.

 

The higher the floor pdu load (which includes the rack pdu load), the greater the simulated impact of 1 or more cooling units failing/being turned off.

 

cooling properties.jpg

 

 
 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-08-03 05:54 AM
0 Likes
0
710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-03 05:54 AM

Re: Cooling unit simulate impact

Hi Venkat,

It seems to be bug (somewhere in the setup), changing power strategy to Predicted Power should not break Impact calculations. I cannot find any reason why this may happen in your setup, so I have added this to our backlogs for debugging.

For the time being you might want to switch to Adjusted Nameplate strategy when running the simulate impact.

Kind regards,

Jef

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
Venkat
Ensign Venkat Ensign
Ensign
‎2020-07-28 01:11 PM
0 Likes
3
784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-28 01:11 PM

Re: Cooling unit simulate impact

Dears

 

Any Suggestion please.

 

Thanks - K.Venkat

Tags (1)
  • Tags:
  • english
Share
Reply
ATrabert
Lieutenant JG ATrabert Lieutenant JG
Lieutenant JG
‎2020-07-28 01:39 PM
1 Like
2
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-28 01:39 PM

Re: Cooling unit simulate impact

Hi Venkat,

What is the cooling capacity of the 3 cooling units individually/combined and how much estimated load and/or predicted load is being used right now?

 

I noticed only one cooling unit was off, since there are still 2 more in the room, they can most likely handle the additional cooling load for the 3rd unit. This is why you are not really seeing any cooling impact.  Also if the power usage is low, this would also explain why you are not seeing much if any cooling impact.

 

What happens when you turn off 2 or all 3 units? 

Tags (1)
  • Tags:
  • english
Share
Reply
Venkat
Ensign Venkat Ensign
Ensign
‎2020-07-30 09:20 AM
0 Likes
1
743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-30 09:20 AM

Re: Cooling unit simulate impact

Hi ATrabert,

 

Thanks. 

 

Now I am getting the simulation impact values for more racks, while de-activate the 1 or 2 Cooling Units. (Predicted power / Adjusted name plate) 

 

There is no measured power value for Cooling Unit and only the Estimated load each Unit having 81kW  as name plate and cooling power. The adjusted name plate consider as 45kW for each Unit.

 

Thanks - K.Venkat.

Tags (1)
  • Tags:
  • english
Share
Reply
ATrabert
Lieutenant JG ATrabert Lieutenant JG
Lieutenant JG
‎2020-07-30 10:10 AM
0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-30 10:10 AM

Re: Cooling unit simulate impact

Hi Venkat,

Glad you're seeing more expected values, I should have been more specific but I was asking for estimated load of room (eg Floor PDU load) and the Cooling Capactiy of the cooling units. CFM would also be relevant.

 

The higher the floor pdu load (which includes the rack pdu load), the greater the simulated impact of 1 or more cooling units failing/being turned off.

 

cooling properties.jpg

 

 
 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-08-03 05:54 AM
0 Likes
0
711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-03 05:54 AM

Re: Cooling unit simulate impact

Hi Venkat,

It seems to be bug (somewhere in the setup), changing power strategy to Predicted Power should not break Impact calculations. I cannot find any reason why this may happen in your setup, so I have added this to our backlogs for debugging.

For the time being you might want to switch to Adjusted Nameplate strategy when running the simulate impact.

Kind regards,

Jef

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
24
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric