Good day,
Is it possible to Connecting a PS100 Particle Sensor to a Netbotz 500 NBRK0570.
(CID:105462359)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:09 PM . Last Modified: 1 week ago
Hi IESLUSER,
It is possible to connect a PS100 Particle Sensor (NBES0201) to a Netbotz 570. You will need to use the Sensor pod 120 (NBPD0122) inconjuction with the Netbotz 570 to connect the Particle Sensor.
You can use this combatility matrix link I have listed below as reference.
Kind Regards,
Andrew
(CID:105462361)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:09 PM . Last Modified: 1 week ago
Hi IESLUSER,
It is possible to connect a PS100 Particle Sensor (NBES0201) to a Netbotz 570. You will need to use the Sensor pod 120 (NBPD0122) inconjuction with the Netbotz 570 to connect the Particle Sensor.
You can use this combatility matrix link I have listed below as reference.
Kind Regards,
Andrew
(CID:105462361)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:09 PM . Last Modified: 1 week ago
The NBPD0122 is an older netbotz sensor pod which still can't connect to the NBRK0570 unit, this can't work.
(CID:108825736)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:09 PM . Last Modified: 1 week ago
As stated in the Compatibility Matrix that I listed above, the NBPD0122 it is compatible with the Netbotz 570. The NBPD0122 connects via a USB Type A to B Cable to the Netbotz 570. Please also see the link to the installation manual for the Netbotz 570, which references how the Sensor Pod 120 is connected to the Netbotz 570 on Page 22 (Page 28 of the PDF). http://dcimsupport.apc.com/download/attachments/92078096/990-3291f-en.pdf?version=1&modificationDate...
(CID:108825737)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:09 PM . Last Modified: 1 week ago
Thank you.
(CID:105467435)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:09 PM . Last Modified: 2023-10-31 10:21 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.