Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Central and DCE on same SNMP LAN
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51003members
Join Now
245054posts
Join Now

Central and DCE on same SNMP LAN

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:05 PM
0 Likes
7
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:05 PM

Central and DCE on same SNMP LAN

This question was originally posted on DCIM Support by Seun Feyisetan on 2018-09-10


Hi,

I have got Central at the moment. I have installed DCE on the same LAN.

If I "discover" from DCE, am I likely to break Central speaking with the current nodes? 

Thanks

(CID:134029261)

Solved! Go to Solution.

Labels
  • Data Center Expert
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:05 PM
0 Likes
4
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:05 PM

Re: Central and DCE on same SNMP LAN

This answer was originally posted on DCIM Support by Steven Marchetti on 2018-09-10


Hi Seun,

There is no specific issue with any 2 monitoring systems monitoring the same SNMP device. There are always chances that too much polling could cause conflicts but as long as the systems are polling at a reasonable rate and the devices are not constantly going into and out of alert, there should be no issue.

Standard polling rates are about once every 5 minutes and should cause no issue. If you do see devices lose comm more often than they do now, just increase timeouts and retries for those devices.

If they were to be sharing the same private or secondary LAN, you'd want to turn off DHCP on one of the systems so that doesn't conflict. I would suggest turning it off on the newly deployed system (before connecting it to that LAN) so devices don't all get new IPs and have to be rediscovered on the old Central server.


Steve

(CID:134029276)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
7 Replies 7
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:05 PM
0 Likes
0
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:05 PM

Re: Central and DCE on same SNMP LAN

This comment was originally posted on DCIM Support by Seun Feyisetan on 2018-09-10


Any idea Steven Marchetti?

(CID:134029269)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:05 PM
0 Likes
4
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:05 PM

Re: Central and DCE on same SNMP LAN

This answer was originally posted on DCIM Support by Steven Marchetti on 2018-09-10


Hi Seun,

There is no specific issue with any 2 monitoring systems monitoring the same SNMP device. There are always chances that too much polling could cause conflicts but as long as the systems are polling at a reasonable rate and the devices are not constantly going into and out of alert, there should be no issue.

Standard polling rates are about once every 5 minutes and should cause no issue. If you do see devices lose comm more often than they do now, just increase timeouts and retries for those devices.

If they were to be sharing the same private or secondary LAN, you'd want to turn off DHCP on one of the systems so that doesn't conflict. I would suggest turning it off on the newly deployed system (before connecting it to that LAN) so devices don't all get new IPs and have to be rediscovered on the old Central server.


Steve

(CID:134029276)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:05 PM
0 Likes
0
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:05 PM

Re: Central and DCE on same SNMP LAN

This comment was originally posted on DCIM Support by Seun Feyisetan on 2018-09-10


Thanks Steve. Will give that a shot.

(CID:134029287)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:05 PM
0 Likes
0
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:05 PM

Re: Central and DCE on same SNMP LAN

This comment was originally posted on DCIM Support by Steven Marchetti on 2018-09-10


Just an FYI, If you were doing (http/https) NetBotz , I don't recommend monitoring them with more than 1 DCE server...definitely not more than 2 especially if using surveillance.

(CID:134029296)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:05 PM
0 Likes
0
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:05 PM

Re: Central and DCE on same SNMP LAN

This comment was originally posted on DCIM Support by Seun Feyisetan on 2018-09-11


Thanks Steve.

Slightly unrelated follow-up question. Can I backup/export my historical data (and probably config/threshold settings) and import these into my new DCE appliance?

(CID:134029600)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:05 PM
0 Likes
0
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:05 PM

Re: Central and DCE on same SNMP LAN

This comment was originally posted on DCIM Support by Steven Marchetti on 2018-09-11


Hi Seun,

 

No. Because of things like changes in design of the database in different versions, you can not import a backup of DCE that is not of the same version to which you are importing. That is to say if you have DCE 7.5, you can only import a backup from another 7.5 system. If you back up a 6.0 server, you can only import that into another 6.0 serer. The server won't even see the backup from another version.

 

Steve

(CID:134029692)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:06 PM
0 Likes
0
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:06 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
23
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric