When trying to apply server upgrade, I select the lst file associated to the 7.8.0 upgrade, however, I do not have an option to apply the upgrade.
What do I do to upgrade the system?
(CID:152079605)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:52 PM . Last Modified: 3 weeks ago
Hi Robert,
I think your upgrade path might be incorrect - I think the correct upgrade path would be 7.7.0 -> 7.7.1 -> 7.8.0.
DCE 7.8.0 download page says "A software update is available from DCE 7.7.1. For earlier versions please contact Tech Support.".
Kind regards
(CID:152079764)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:51 PM . Last Modified: 3 weeks ago
Dear Robert Maday,
Can you show a couple of screenshots of your problem? And then they will help you better and faster 😀.
With respect.
(CID:152079616)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:51 PM . Last Modified: 3 weeks ago
From the apply server update, I choose Import,
Select the proper LST file as below.
Then it bounces back to the original one without any information from the pkg that I selected.
(CID:152080467)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:51 PM . Last Modified: 3 weeks ago
Checked upgrade zip-file checksum? Is she correct?
(CID:152080471)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:52 PM . Last Modified: 3 weeks ago
Dear Robert Maday,
I suspect, that this may be a known problem, which is described in topics Update ISX Central 6.3.0 -> 7.0.0: nothing to update? and .
That is, you may need to clean install DCE-7.7.0 server and deploy your full backup to it. Only after that will it be possible to upgrade to DCE-7.8.0.
Hope this helps you.
With respect.
(CID:152079772)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:52 PM . Last Modified: 3 weeks ago
Hi Robert,
I think your upgrade path might be incorrect - I think the correct upgrade path would be 7.7.0 -> 7.7.1 -> 7.8.0.
DCE 7.8.0 download page says "A software update is available from DCE 7.7.1. For earlier versions please contact Tech Support.".
Kind regards
(CID:152079764)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:52 PM . Last Modified: 3 weeks ago
7.71 - Installing now - Had to contact Tech Support and prove valid software support.
Robert
(CID:152080787)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:52 PM . Last Modified: 3 weeks ago
Many thanks for the update, Robert
Kind regards
(CID:152080904)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:52 PM . Last Modified: 3 weeks ago
Confirmed the .zip file checksum is valid.
(CID:152080473)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:52 PM . Last Modified: 2023-10-20 05:07 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.