Hi Team ,
Our DCE monitor some third-party device like RackCDU , their water temp almost over 50 degree, I saw our DCE only can set to max 50 , can we make a change for this threshold maybe
80 degree ? There are still some sensor under high temp environment like transformer etc..
Your comment would be appreciated.
Best Regards
(CID:130092638)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:15 PM . Last Modified: 3 weeks ago
Billy,
How about using 'Other Numeric" instead of "Temperature"?
Select Other Numeric, then maximum threshold.
You should be able to set the maximum value to 80.
p.s you might want to mask of the ip address, team viewer details or other stuff.Or simply set to internal... 😀
(CID:130092650)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:15 PM . Last Modified: 3 weeks ago
Billy,
How about using 'Other Numeric" instead of "Temperature"?
Select Other Numeric, then maximum threshold.
You should be able to set the maximum value to 80.
p.s you might want to mask of the ip address, team viewer details or other stuff.Or simply set to internal... 😀
(CID:130092650)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:15 PM . Last Modified: 2023-10-20 05:06 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.