Hi Michael,
Single phase Easy-UPS use the generic SNMP UPS mib and would easily be monitor-able by either DCE or NetBotz with a 5 node monitoring pack. I would suggest using DCE as you can provide more resources and that is it's main purpose.
The 3 phase units have their own MIB. DCE by default does not have a DDF added to the system for this UPS. You would want to use the DDF menu at the top of the page to request a DDF for it. As for the NetBotz appliances, I do not believe DDFs are being actively created for the NetBotz so if that is indeed the case, you wouldn't be able to monitor it using the 570.
Thanks,
Steve.
(CID:140710957)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:43 PM
This comment was originally posted on DCIM Support by spezialist on 2019-04-01
Dear Michael Ng,
Tell us, please, did you solve your question or not?
With respect.
(CID:141269243)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:43 PM . Last Modified: 2023-10-20 05:06 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.