This question was originally posted on DCIM Support by Bruce Phillips on 2020-01-07
Hi
I am trying to update as below.
Our version is Server Build: 7.7.0.148
The upgrade version upgrade-7.8.0.47
When I try an upgrade it wont import the nbcpkg.lst file.
Can it go from our current version to the new version or does it require the version in-between first? I believe there was a version 7.7.1
thanks
Bruce
(CID:153551940)
This answer was originally posted on DCIM Support by Bruce Phillips on 2020-01-07
The answer to the above is yes you do.
(CID:153551952)
This answer was originally posted on DCIM Support by spezialist on 2020-01-08
Dear Bruce Phillips,
You are right: as follows from User assistance for StruxureWare Data Center Expert 7.x:
If you have more questions, please ask.
With respect.
(CID:153552099)
This answer was originally posted on DCIM Support by Jackie Lehr on 2020-01-09
Hi Bruce Phillips,
The update to DCE 7.8.0 requires that your DCE is at 7.7.1.
The update path and instructions are always in the release notes for each version. You can see the release notes for the most recent version in the DCE documentation or in the PDF Library here in the help center, or on a DCE product page on apc.com.
Best,
Jackie
(CID:153552516)