Dear Team,
how can i add and monitor Samsung camera (Model QND-7080R) in Struxureware DCE.
(CID:126173698)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 01:43 AM . Last Modified: 3 weeks ago
Hi Ali,
As far as I know, the only supported cameras in DCE (through NetBotz) are Pelco cameras.
You can see the list of supported cameras here:
https://www.schneider-electric.us/en/faqs/FA158450/
/Christian
(CID:126173738)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 01:43 AM . Last Modified: 3 weeks ago
Dear Ali,
Do you want to just get a picture from this camera in DCE-client or do you need to monitor the physical state this camera via SNMP (for example, the temperature inside the camera, its alerts, etc.)?
With respect.
(CID:126173923)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 01:43 AM . Last Modified: 2023-10-20 05:05 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.