Hi Team ,
Can Netboz firmware V4.5.4 support TLS1.2 ?
If it can ,how can we enable it ? If not , when will it be available ?
(CID:116919234)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:04 PM
This answer was originally posted on DCIM Support by John Thompson on 2017-04-11
Hi Eric,
TLS 1.2 has been supported since v4.5.2, so it should be enabled by default.
See the Release Notes for each version on the page below.
https://dcimsupport.apc.com/display/public/SWDCDOC/PDF+Library#PDFLibrary-ReleaseNotesadditional.1
Regards
(CID:116919314)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:04 PM
This answer was originally posted on DCIM Support by John Thompson on 2017-04-11
Hi Eric,
TLS 1.2 has been supported since v4.5.2, so it should be enabled by default.
See the Release Notes for each version on the page below.
https://dcimsupport.apc.com/display/public/SWDCDOC/PDF+Library#PDFLibrary-ReleaseNotesadditional.1
Regards
(CID:116919314)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:04 PM . Last Modified: 2023-10-20 05:05 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.