  • Battery Age says zero (0) but they are actually 11-months old
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49540members
Join Now
242902posts
Join Now

Battery Age says zero (0) but they are actually 11-months old

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:17 PM
0 Likes
17
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:17 PM

Battery Age says zero (0) but they are actually 11-months old

This question was originally posted on DCIM Support by John Beck on 2019-01-17


Battery Age says zero (0) but they are actually 11-months old

(CID:138381764)

Labels
  • IT Expert
Share
  • All forum topics
  • Previous Topic
  • Next Topic
17 Replies 17
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:17 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:17 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by spezialist on 2019-01-17


Dear John Beck,

What is the UPS model?

What is NMC firmware?

What is the software version of the gateway?

Show a couple of screenshots from the NMC and from the gateway software with the your problem so that you can be helped more quickly.

With respect.

(CID:138381787)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:17 PM
0 Likes
2
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:17 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This answer was originally posted on DCIM Support by John Beck on 2019-01-17


From the NMC:

 

(CID:138381803)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:17 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:17 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by Ralph Berrett on 2019-01-18


The "Battery Age" is calculated via the "Last Battery Replacement" date.  If that is not set it uses the "UPS Manufacture Date".  Is the "UPS Age" sensors showing the expected value?

 

You might try manually changing the "Last Battery Replacement" date.

(CID:138807114)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:17 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:17 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by John Beck on 2019-01-18


I did manually change the "Last Battery Replacement" date as follows:

 

And then I did a re-discover of the UPS and EcoStruxure IT still displayed a Battery Age of:  "0 ms".

(CID:138807123)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:17 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:17 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by John Beck on 2019-01-17


I just updated the Gateway today from 1.4.3.9 to 1.5.0.66

(CID:138381809)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:17 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:17 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by John Beck on 2019-01-17


The Model of the UPS is as follows:

 

 

(CID:138381811)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:17 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:17 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by John Beck on 2019-01-17


NMC Firmware:

 

(CID:138381814)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:17 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:17 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by John Beck on 2019-01-17


Battery Age from the Gateway:

 

(CID:138381817)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:18 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:18 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by John Beck on 2019-01-17


And I also did a re-discover.

(CID:138381819)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:18 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:18 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by spezialist on 2019-01-18


Dear John Beck,

Great, thanks for the detailed information 😀.

By the way, I found another place where you can get guaranteed help on your problem with the EcoStruxure IT Expert digital service: https://ecostruxureit.com/request-support/ .

To speed up the resolution of your problem, I recommend that you do Submit a ticket on the above resource.

With respect.

(CID:138381913)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:18 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:18 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by John Beck on 2019-01-18


I tried to Submit a ticket that service and received the following:

 

(CID:138807109)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:18 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:18 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by spezialist on 2019-01-18


What exactly file format are you trying to upload?

(CID:138807137)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:18 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:18 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by John Beck on 2019-01-18


Microsoft Word Document.

(CID:138807143)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:18 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:18 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by spezialist on 2019-01-18


Dear John Beck,

I highly recommend uploading screenshots in a standard image format, for example, jpg, png, tif, etc. or zip  archive file format, and not in MS Word text document format 😀.

With respect.

(CID:138807225)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:18 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:18 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by spezialist on 2019-02-09


Dear John Beck,

Tell us, please, did you solve your problem or not?

With respect.

(CID:139693949)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:18 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:18 PM

Re: Battery Age says zero (0) but they are actually 11-months old

This comment was originally posted on DCIM Support by John Beck on 2019-02-11


No. And this issue is on more than one of our UPS's.

(CID:139694275)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:18 PM
0 Likes
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:18 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric