HI,
We need a solution to integrate UPS with DCE. UPS is connected to BMS via Simens controller as gateway Bacnet over IP protocol. How can i access this Bacnet IP on DCE?
(CID:134036860)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:11 AM . Last Modified: 2 weeks ago
Hi Shaik,
DCE can't communicate using Bacnet. I believe there are gateways out there that can translate...do Bacnet to Modbus. If you can do that, we can monitor via Modbus.
Steve
(CID:134036873)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:11 AM . Last Modified: 2 weeks ago
Hi Shaik,
DCE can't communicate using Bacnet. I believe there are gateways out there that can translate...do Bacnet to Modbus. If you can do that, we can monitor via Modbus.
Steve
(CID:134036873)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:12 AM . Last Modified: 2023-10-20 05:02 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.