EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:58 PM . Last Modified: 3 weeks ago
When we logon to the application the error "An Error has occurred and your changes may not have been saved": pops up and the application closed.
DCO 8.2.7.77109
(CID:134028822)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:58 PM . Last Modified: 3 weeks ago
Hi Andrew,
All users having this issue during the login, right? Do you know when this happened, what you/user have done or have been doing just before this issue?
Apparently something in the setup generating this exception & we need to find out what, would it be possible to ask for the following data:
copy of the backup
client application.log file (usually located in C:\Users\
server logs (can be downloaded from webmin interface, StruxureWare DC Operation>Download Log Files>"Download log files")
I will send you an invite to my =S= box so the data can be safely shared with me (if you would), thanks.
Kind regards
(CID:134028883)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:58 PM . Last Modified: 3 weeks ago
Hi Andrew,
Same issue seems to have been reported to CCC. The room opening issue appears to be related to unsupported power path on a rack ats device, that is currently connected to racks single rack pdu.
To resolve the issue you would need to edit the device Properties (via desktop client and Equipment Browser) and modify its Power dependency settings to undefined.
I will send you more info by direct email soon, thanks.
Kind regards
(CID:134029829)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:58 PM . Last Modified: 2023-10-20 05:00 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.