  • Alarms from Netbotz 250 not being seen / triggered immediately in DCE
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49522members
Join Now
242868posts
Join Now

Alarms from Netbotz 250 not being seen / triggered immediately in DCE

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:53 PM
0 Likes
5
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:53 PM

Alarms from Netbotz 250 not being seen / triggered immediately in DCE

This question was originally posted on DCIM Support by Steve McLaughlin on 2018-08-17


Hello,

We have a number of Netbotz 250 devices that we are monitoring with DCE via SNMPv3.

According to what we have read, DCE configures the Netbotz 250 with a hidden trap receiver destination (priority scanning) so that alarms that are generated on the Netbotz send a trap immediately to DCE and then it is supposed to scan the Netbotz for the alarm information and take action accordingly.

We can see in our logs that the Netbotz 250's are sending these traps to the DCE but it is not alerting or indicating that an alarm has occurred.

Example:

Door sensor open/close - if there are multiple open / close alarms these generate a trap to the DCE for each instance however it shows nothing in its alarm history

We also have the DCE setup to poll the devices every minute and occasionally it will pick up a door alarm if it has occurred and is active at the same time as the poll.

However this is not ideal as we are relying on DCE to perform the monitoring and alerting and to keep a history of all the alarms that have occurred.

When the trap is sent from the Netbotz to DCE is this supposed to generate the alarm immediately or does that only occur if the alarm is still active when DCE scans the netbotz after the trap is received ?

The Netbotz 450 devices we have monitored via DCE never miss an alarm and all alerts are recorded by DCE.

Just trying to understand if this is expected for APC SNMP monitored devices or if something is not configured / working correctly.

Thanks,

 

Steve

(CID:133372955)

Solved! Go to Solution.

Labels
  • Data Center Expert
  • NetBotz
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:53 PM
0 Likes
3
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:53 PM

Re: Alarms from Netbotz 250 not being seen / triggered immediately in DCE

This answer was originally posted on DCIM Support by Steven Marchetti on 2018-08-17


Hi Steve,

 

The priority scanning option is the hidden trap receiver process to which you're referring. As long as it is set up properly, your 250 goes into alert and sends a trap. DCE does nothing with this trap other than puts that device next to be scanned. This is to rule out any potential false alarms.

When DCE then polls the device, it polls a specific alarm OID and if there is information available, it reads the data then based on the configuration both in the DDF that gets downloaded from the APC device (creates the device alarm info in DCE) and your configuration on that page, it alerts or doesn't.

If the event happens so quickly that the device sends a trap but the poll does not see any data in the alarm OID, it will not alert. If on the other hand, you've blocked the write community string on the device / network / firewall, or if you've not configured priority scanning, the device will not be scanned until it's next scheduled poll. This could take anywhere from a few seconds up to (if using defaults) 5 minutes. 

 

Thanks,

Steve

 

 

(CID:133372960)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:53 PM
0 Likes
3
151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:53 PM

Re: Alarms from Netbotz 250 not being seen / triggered immediately in DCE

This answer was originally posted on DCIM Support by Steven Marchetti on 2018-08-17


Hi Steve,

 

The priority scanning option is the hidden trap receiver process to which you're referring. As long as it is set up properly, your 250 goes into alert and sends a trap. DCE does nothing with this trap other than puts that device next to be scanned. This is to rule out any potential false alarms.

When DCE then polls the device, it polls a specific alarm OID and if there is information available, it reads the data then based on the configuration both in the DDF that gets downloaded from the APC device (creates the device alarm info in DCE) and your configuration on that page, it alerts or doesn't.

If the event happens so quickly that the device sends a trap but the poll does not see any data in the alarm OID, it will not alert. If on the other hand, you've blocked the write community string on the device / network / firewall, or if you've not configured priority scanning, the device will not be scanned until it's next scheduled poll. This could take anywhere from a few seconds up to (if using defaults) 5 minutes. 

 

Thanks,

Steve

 

 

(CID:133372960)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:53 PM
0 Likes
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:53 PM

Re: Alarms from Netbotz 250 not being seen / triggered immediately in DCE

This comment was originally posted on DCIM Support by Steve McLaughlin on 2018-08-17


Thanks for the quick reply.

That is what I thought was happening.

Not ideal for door sensors which can trigger / clear very quickly.

Ok for smoke/water/temp and other "slow moving" sensors.

At least we know it is working as designed.

Thanks for your help.

(CID:133372968)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:53 PM
0 Likes
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:53 PM

Re: Alarms from Netbotz 250 not being seen / triggered immediately in DCE

This comment was originally posted on DCIM Support by Steven Marchetti on 2018-08-17


No problem. Just an FYI about the 450 though, they work totally different. They do all their own alerting and then just store the alert on DCE pushing it using http or https. 

(CID:133372974)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:54 PM
0 Likes
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:54 PM

Re: Alarms from Netbotz 250 not being seen / triggered immediately in DCE

This comment was originally posted on DCIM Support by Steve McLaughlin on 2018-08-17


Thanks, realize that now about the 450.

In retrospect we should have standardized on all 450's instead of a mix of 450's and 250's.

(CID:133372982)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:54 PM
0 Likes
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:54 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric