This question was originally posted on DCIM Support by Shoaib Maqsood on 2019-06-12
Hello,
I have installed 5 ATS (AP4423 6.5.1 OS). These are properly integrated with DCE (version 7.4.1). But we are facing an issue. Under the (create threshold) window voltage tab is not highlighted. we cannot access the voltage tab for threshold setting.
(CID:144868992)
This answer was originally posted on DCIM Support by Balaraman Jagadeesan on 2019-06-12
Dear Shoalb,
Do you see Voltage as a sensor value for this device in DCE under view Device Sensor Value?
If not, DCE will not allow you to create a threshold for the sensor value that is not available as a sensor.
I noticed that the latest AP44XX Series Rack ATS Unit Firmware Revision 6.5.6 is now available.
I believe that you should be able to see the voltage as sensor value via SNMP protocol after you upgrade the ATS firmware to the latest firmware version. You can find ATS4G 6.5.6 for download in the DCE firmware catalog or download from the below link.
https://www.apc.com/in/en/tools/download/index.cfm
If you still do not see the voltage as a sensor value in DCE, then the Device Definition File(DDF) update in DCE may be required.
Secondly, I request you to upgrade DCE version 7.4.1 to the latest version 7.6.0 for better performance of DCE even though it is not related to this topic. The latest DCE version come with the latest pre-loaded APC devices DDF already.
(CID:144869076)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!