Posted: 2020-07-02 05:58 PM
This question was originally posted on DCIM Support by Peter Wang on 2015-11-24
Dear experts,
We had a AP9465 the status indicator LEC amber is blinking, I check the doc, it says the system has detected an error, but what kind of error it is and how to solve it ?
We checked the DCE , no alarms shows.
thanks!
(CID:104188982)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 05:58 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2015-11-24
Hi Peter,
The AP9465 is based on a Dell server. Please provide the Dell service tag, the MAC address of the server, and the Dell service tag to your local APC / Schneider tech support. If it's under warranty, they should be able to assist you with correcting hardware issues / replacement if necessary. Your server is likely a Dell R200 or R210 but without that data (and I wouldn't want you to provide it on an open forum) I can not say with any certainty. There is also a display on the server and when there is an error, this display will usually show an error code which also may assist in any hardware troubleshooting.
Thanks,
Steve
(CID:104189019)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 05:58 PM
This comment was originally posted on DCIM Support by Jesper Bjerregård on 2015-11-24
Can you please provide the capturelogs to diagnose the errors? To gather the needed logs please browse to http://<your_server_ip>/capturelogs You will be prompted to input credentials, once the page has loaded please click on "Create Server Log Archive". After the process has been completed please download and provide them to the team. Thanks Jesper
(CID:104188985)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 05:58 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2015-11-24
Hi Peter,
The AP9465 is based on a Dell server. Please provide the Dell service tag, the MAC address of the server, and the Dell service tag to your local APC / Schneider tech support. If it's under warranty, they should be able to assist you with correcting hardware issues / replacement if necessary. Your server is likely a Dell R200 or R210 but without that data (and I wouldn't want you to provide it on an open forum) I can not say with any certainty. There is also a display on the server and when there is an error, this display will usually show an error code which also may assist in any hardware troubleshooting.
Thanks,
Steve
(CID:104189019)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 05:58 PM . Last Modified: 2023-10-31 10:15 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.