we have a 4 panel main room pdu and can add sensor mapping to 2 of those panels, but not to 2 x others and can't understand why. Other multiple panel pdu's can have sensor mapping without any issues.
(CID:105466877)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:24 AM . Last Modified: 2 weeks ago
Hi all,
Just a small note that this is/will be investigated off-line.
Kind regards
(CID:105467796)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:24 AM . Last Modified: 2 weeks ago
Hi Pete It should of course work for all PDUs, but it is difficult to see what is the issue without more information. Do you have a screenshot of the setup that you can share? That would be a start to try and reproduce the issue. Best, Niels
(CID:105466886)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:24 AM . Last Modified: 2 weeks ago
Hi all,
Just a small note that this is/will be investigated off-line.
Kind regards
(CID:105467796)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:24 AM . Last Modified: 2 weeks ago
Hi all, In short, customized DDF file did fix the issue, so the device could be associated to its corresponding model in DCO. Kind regards
(CID:105469538)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:25 AM . Last Modified: 2023-10-31 10:12 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.