I’m searching a solution to connect 20 x 4-20mA sensor readings to the DCE system.
The NetBotz 570 support 4 x 4-20mA sensors input. I have found in the manual that I can connect 4-20mA Input Pod 120, which is discontinued, the replacement is NBPD0129.
I haven’t found documentation for this input pod 120 and the Netbotz 570 connection.
How many pod can I connect to the Netbotz 570?
This type of Input modul is connected via USB cabel?
Does it need external power supply?
There is another solution to connect external 4-20mA sensors to the DCE system?
(CID:152077250)
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-11-20
Hi Gabor,
The NBPD0129 IS the old 4-20 sensor pod. The documentation for the pod can be found here:
The pod connects via USB. There is nothing different about the connection to the 570 than there was from the old 420 or 500 models. All configuration should be nearly identical.
Steve
(CID:152077265)
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-11-20
Hi Gabor,
The NBPD0129 IS the old 4-20 sensor pod. The documentation for the pod can be found here:
The pod connects via USB. There is nothing different about the connection to the 570 than there was from the old 420 or 500 models. All configuration should be nearly identical.
Steve
(CID:152077265)
This comment was originally posted on DCIM Support by Gabor Novak on 2019-11-20
Hi Steve,
If I want to connect 12 pods, how can I make this?
There is just 4 usb port on the Netbotz 570.
The pod is powered through the USB cable?
(CID:152077272)
This comment was originally posted on DCIM Support by Steven Marchetti on 2019-11-20
Hi Gabor,
You'd want to use powered USB hubs.
Steve.
(CID:152077274)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!