EcoStruxure Geo SCADA Expert Forum
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Posted: 2021-07-20 05:58 AM . Last Modified: 2023-05-03 12:02 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-20 05:58 AM . Last Modified: 2023-05-03 12:02 AM
Good morning
I would need to count the hours in which a bit is ON. such as the hours in which an engine is active.
is it possible to do it with the logic of Geo scada?
is there an internal clock?
can I count the seconds with an internal variable?
How can I create it?
I do not have the possibility to modify the device connected to Geoscada, so I have to operate on Geoscada.
Thank you all
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-20 06:07 AM
You should be able to do this with a Runtime Accumulator.
It shouldn't require a logic program.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-20 06:07 AM
You should be able to do this with a Runtime Accumulator.
It shouldn't require a logic program.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-21 05:56 AM
Thanks for the help! I solved it using an accumulator
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.