Hello Everyone,
We're trying to load history data using C# following this link
Solved: Using automation interface with C# to load history - Communities (se.com)
but an exception was thrown
Exception Details: System.Runtime.InteropServices.COMException: Type mismatch. (Exception from HRESULT: 0x80020005 (DISP_E_TYPEMISMATCH))
Our Code:
ScxV6Server Svr = new ScxV6DbClient.ScxV6Server();
Svr.Connect("xxx", "xx", "xxx");
ScxV6Object csObj = Svr.FindObject("xxx");
object Historic = csObj.Interface.GetType().InvokeMember("Historic", System.Reflection.BindingFlags.GetProperty, null, csObj.Interface, null);
if (Historic != null) {
Historic.GetType().InvokeMember("LoadDataValue", System.Reflection.BindingFlags.InvokeMethod, null, Historic, new Object[] { 1, 192, "2022-02-21 10:09:05", 48.2 }); // the exception thrown at this line
}
Svr.Disconnect();
any help appreciated
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-21 04:31 AM
In the arguments to the LoadDataValue method you've used a string for the time, which is the wrong type and likely the cause of the type mismatch exception.
You should use a System.DateTimeOffset for times:
https://docs.microsoft.com/en-us/dotnet/api/system.datetimeoffset?view=netframework-4.8
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-21 04:52 AM
We've replaced with DateTime and it worked just fine
string t = (DateTime.Now.ToString());
Historic.GetType().InvokeMember("LoadDataValue", System.Reflection.BindingFlags.InvokeMethod, null, Historic, new Object[] { 1, 192, t, 148.12 });
thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-21 04:31 AM
In the arguments to the LoadDataValue method you've used a string for the time, which is the wrong type and likely the cause of the type mismatch exception.
You should use a System.DateTimeOffset for times:
https://docs.microsoft.com/en-us/dotnet/api/system.datetimeoffset?view=netframework-4.8
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-21 04:39 AM
We've changed the time as suggested
Historic.GetType().InvokeMember("LoadDataValue", System.Reflection.BindingFlags.InvokeMethod, null, Historic, new Object[] { 1, 192, DateTimeOffset.Now, 48.2 });
another exception where thrown
Exception Details: System.ArgumentException: Value does not fall within the expected range.
any hint
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-21 04:52 AM
We've replaced with DateTime and it worked just fine
string t = (DateTime.Now.ToString());
Historic.GetType().InvokeMember("LoadDataValue", System.Reflection.BindingFlags.InvokeMethod, null, Historic, new Object[] { 1, 192, t, 148.12 });
thanks