[Imported] Scadapack trend sample data
EcoStruxure Geo SCADA Expert Forum
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-0512:55 PM. Last Modified: 2023-05-0312:36 AM
[Imported] Scadapack trend sample data
>>Message imported from previous forum - Category:ClearSCADA Software<< User: florian, originally posted: 2018-10-24 22:02:54 Id:210 This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.
----------------
**_ebennett:_** **_Hi_**
**_I have setup the RTU to trend pulse counts every 15mins. One record logs the change and the other logs the current value.The RTU creates files which I can retrieve using E Configurator. In CS I have setup the Trend points and they only seem to update when I manually retrieve them by right clicking on the RTU, where do I set up the file uplad Frequency ?_**
**_Cheers_**
-------------
dmercer: I've never used these before, but the help doc goves you this information at:
Driver Reference DNP3 SCADAPack E Driver Configuring DNP3 SCADAPack E Trend Sampler Functionality Example Configuration
The outstation should have SCADAPack Tab. In that tab under Trend Retrieval you can set when CS will retieve the tend data from the RTU.
---------------------
bevanweiss: I would not recommend using Trend Points. They are incredibly specific to SCADAPack RTUs, and aren't really 'standard' in any means.
If you want a trend, you can get the same by using normal DNP3 points which are historised.
If you have the pulse counter feeding a DNP3 Counter point (as happens by default) then you just configure a Class against the counter, and a deadband for the events to be generated. When ClearSCADA does a poll then it will retrieve the DNP3 event records for the Counter point, and you'll have your trend available...