[Imported] Clear Scada and siemens s71200 communication via DNP3
EcoStruxure Geo SCADA Expert Forum
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-0512:38 PM. Last Modified: 2023-05-0312:36 AM
[Imported] Clear Scada and siemens s71200 communication via DNP3
>>Message imported from previous forum - Category:ClearSCADA Software<< User: arjunmurali, originally posted: 2018-10-24 08:31:21 Id:184 Hi, We use clear scada 2010 R1 in CCR and Siemens S7-1200 PLC in remote site communicating via dnp3 protocol via gprs modems , the issue we face is in the pump running trends which are not updating in the scada all time,also the pumps running trends are not matching with the level and flow trends in the site. Is there any issue in the data buffering of the plc or any settings to change in polling of sites to make it normal.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-0512:39 PM
>>Responses imported from previous forum
Reply From User: sbeadle, posted: 2018-10-24 09:55:25 Are the pump trends fed directly from DNP3, or are you using an Accumulator object? If the latter, you could use the Continuous option, but that will read incorrectly if your modem fails to connect. Really you can't expect live displays from a GPRS source.