EcoStruxure Geo SCADA Expert Forum
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-27 10:08 AM . Last Modified: 2023-05-03 12:16 AM
I'm looking to determine what version/release of DNP3 and Secure Key Authentication is implemented in ClearSCADA 2017R2 and R3 and 2019. We are researching alternative field equipment and need to know what CS/GS will support.
Thanks in advance for any assistance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-27 10:38 AM
All versions support IEEE 1815-2012 (the current DNP3 standard) however that doesn't really tell you very much as most features in the DNP standard are optional.
All versions support DNP Secure Authentication version 2 (SAv2)
You really want to look at the DNP device profile to get detailed information on what features and options are supported. The device profiles are installed into the "C:\Program Files\Schneider Electric\ClearSCADA\InteropDocuments" folder by default.
See "Geo SCADA Expert DNP Master Device Profile.xml" or "ClearSCADA DNP Master Device Profile.xml".
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-27 10:38 AM
All versions support IEEE 1815-2012 (the current DNP3 standard) however that doesn't really tell you very much as most features in the DNP standard are optional.
All versions support DNP Secure Authentication version 2 (SAv2)
You really want to look at the DNP device profile to get detailed information on what features and options are supported. The device profiles are installed into the "C:\Program Files\Schneider Electric\ClearSCADA\InteropDocuments" folder by default.
See "Geo SCADA Expert DNP Master Device Profile.xml" or "ClearSCADA DNP Master Device Profile.xml".
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-27 11:09 AM
Thanks for the reply Andrew!
Appreciate the info.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.