Can i simulate the Geo SCADA expert with Modbus tcp with EcoStructure control expert on single PC?
EcoStruxure Geo SCADA Expert Forum
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-1409:06 PM
You're going to need to explain what you mean by 'simulate the GeoSCADA expert'.
If you actually just want to simulate a ModbusTCP client connecting to the ModbusTCP server implementation on your PLC, then you could use ModScan. It's commercial software, but it's reliable and easy to use.
If you instead mean that you want to simulate your 'field device', i.e. you want to simulate your PLC, then you could use ModSim (also commercial software).
There are free versions of other Modbus clients / servers available, however I've never found them to be quite as good / reliable as ModScan / ModSim.
If you mean something else entirely... then you should try wording your question again.
Lead Control Systems Engineer for Alliance Automation (VIC). All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..