Learn about the Community. Join our Core Community to Get Started

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
EDC Forum
cancel
Showing results for 
Search instead for 
Did you mean: 
Highlighted
Lieutenant JG

ComX Extract Task Fails

Hello there. I'm using EDC v3.7.52.1 and the ComX Extract Task is failling. I've attached an example csv file that would fail. The error message I'm getting when attempting to run the task shows:

201907171658152629199EDC_Job_NKSStockholm,2019-07-17 16:58:18.950,ERROR,aos-misc-prod\JGivens,ComX Invalid File Info,Input File 'F:\EDC\DataFiles\NKSStockholm\01.FTPDownload\PLC_20190717091500.csv' is invalid. Error 'Invalid header. Expected '8' tags; but '1' found.',,

201907171658152629199EDC_Job_NKSStockholm,2019-07-17 16:58:18.950,ERROR,aos-misc-prod\JGivens,ComX Invalid File Info,Input File 'F:\EDC\DataFiles\NKSStockholm\01.FTPDownload\PLC_20190717091500.csv' is invalid. Error 'Invalid header. Expected '8' tags; but '1' found.',,

201907171658152629199EDC_Job_NKSStockholm,2019-07-17 16:58:18.950,ERROR,aos-misc-prod\JGivens,ComX Unexpected Number Of Values,File: 'F:\EDC\DataFiles\NKSStockholm\01.FTPDownload\PLC_20190717091500.csv' Line: '8'. Number of values does not match the number of topics,,

201907171658152629199EDC_Job_NKSStockholm,2019-07-17 16:58:18.950,ERROR,aos-misc-prod\JGivens,ExtractTask FileSplitter,Exception of type 'SE.Common.Logging.HandledException' was thrown.,,

 

I'm trying to process many of these csv files, but atached is an example (the one referenced in the error message); however, all csv files have the same basic layout, and all of the csv files are producing that same error message. Thanks in advance!

 

**EDIT** I kept getting error messages when attempting to attach the csv file, so I just had to post without it. I've uploaded it to BOX and it can be found here:

https://schneider-electric.box.com/s/6035rl9fegnmbgznxy9gafybloo860l6

 

6 REPLIES 6

Re: ComX Extract Task Fails

Hi Jeffrey,

I'll look into this.

Thomas

Re: ComX Extract Task Fails

Hi Jeffrey,

Can you please share the EDC Job file and let me know what EDC version you are using? 

Thanks,

Tom

 

Lieutenant JG

Re: ComX Extract Task Fails

Hi Tom,

 

I've attached the job file. EDC Version 3.7.52.1

Re: ComX Extract Task Fails

Hi Jeffrey,

 

I'm pretty sure that the Com'X and EGX extract tasks only work with comma as a delimiter, not with semicolon:

 

https://community.exchange.se.com/t5/EDC-Forum/How-to-set-up-ComX200-to-send-data-to-a-central-repos...

 

Also, since you're using custom measurements, I'd expect some work mapping those manually, if not needing a Python extract task instead of the standard COM'X task

 

Hope it helps

 

 

Lieutenant JG

Re: ComX Extract Task Fails

Thanks for the prompt response. I informed the Engineer that handles this customer to see if they can swap to 'comma' separators instead of semicolons. Once we get this adjustment, I'll let you know if the task succeeds or fails. No timeline on execution is known at this point, though.

Lieutenant JG

Re: ComX Extract Task Fails

Just letting everyone here know that modifying the delimiter to be a comma DID resolve the task failures we were experiencing. Additionally, it should be noted that the Default "date format" had to be modified as well. The task expected the format "YYYY-MM-DD" by default, but the ComX was sending "DD-MM-YYYY" ...fortunately, there is a setting in the task to change this to DD-MM-YYYY so it was an easy resolution. Thanks for the help. Cheers!