Third Party BACnet devices go offline when fix for defect 38618 is applied to site.
In this case a Luton GW was using Network Number 1 for its virtual network number and this was conflicting with the use of Network Number 1 on the primary BACnet interface of EBO, which is a BACnet routing error. EBO servers ignore messages from other BACnet devices, when those messages contain BACnet Source Network information matching the configured BACnet network number for EBO's primary BACnet interface. |
45125 | Function as Design: set the network number on the Lutron virtual network to a unique network number for that site | HFL 2020-09-17 |