Is it possible to slow down the internal PID so that a under floor heating does not overheat?
Or do we need to write a LUA script to control the output directly?
Has anyone one such a system yet?
Hello,
Only the proportional band is configurable on the SE8300 (from 3F to 10F). I would recommend a LUA script that takes into account the slab temperature and reacts accordingly.
Patrick Dumas from the Montreal Viconics office might have a script already done or can provide some insight. You can reference me as Patrick and I both joined Schneider when Viconics was acquired in 2011.
Michael Colicchio