I am receiving the following error in the Event log when logging into the server running CentOS 6.6 and PowerChute Network Shutdown 3.10 for Linux at [https://[server IP]:6547]:
Connection error because PowerChute received an untrusted SSL certificate from [https://[Mgmt Card IP address:443]. Please enable the option "Accept Untrusted SSL Certificates" on the Network Management Card Connection page or add the certificate to the PowerChute keystore. [More Information]
The only place I can find where the "Accept Untrusted SSL Certificates" setting can be changed is via the "Install Wizard", which is accessible via the web interface once PCNS is installed. Even though I confirmed that this setting was already set as directed, I went ahead and ran the wizard anyway to reset the setting and still receive the same error message. The management card is an AP9619 with latest firmware installed.
Is this a known bug?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:38 AM . Last Modified: 4 weeks ago
Wow, I would have thought this would have been made clear during the setup process, or I wouldn't have wasted my time trying to get that to work securely.
Good to know, thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:38 AM . Last Modified: 4 weeks ago
Phil,
There is no HTTPS solution/support for PowerChute v3.1 registering over HTTPS with an AP9617, AP9618, AP9619. If you required SSL the NMC should be upgraded to a AP9631.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:38 AM . Last Modified: 4 weeks ago
Wow, I would have thought this would have been made clear during the setup process, or I wouldn't have wasted my time trying to get that to work securely.
Good to know, thanks.