APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:11 AM . Last Modified: 2024-03-08 01:26 AM
Command: web -lsd enable
NMC info
AP9640
Application Module v1.3.3.1
APC OS v1.3.3.1
Boot Monitor v1.1.0.2
I've verified it works setting it via the web interface, but when trying via CLI it reports success, but then I get this when I query the settings. I even tried rebooting the card.
user>web
E000: Success
Http: disabled
Https: enabled
Http Port: 80
Https Port: 443
Minimum Protocol: TLS1.2
Limited Status Access: disabled
Lim. Status Page Used: n/a
TLS1.2 Cipher Suite Filter: 4
Any suggestions?
Regards, tom
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:11 AM . Last Modified: 2024-03-08 01:25 AM
Thanks Bill. I tried to come back and update that I'd figured it out, but the site wasn't working, then I forgot.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:11 AM . Last Modified: 2024-03-08 01:25 AM
Hi,
You first need to enter web -lsp enable to display a read-only, public web page with basic device status. Then enter web -lsd enable to have the limited status page be the default page when entering the ip/hostname.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:11 AM . Last Modified: 2024-03-08 01:25 AM
Thanks Bill. I tried to come back and update that I'd figured it out, but the site wasn't working, then I forgot.