APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:28 AM . Last Modified: 2024-03-11 02:36 AM
I have a SUA1000RM2U that has a loud buzzing and humming in the transformer. When the AC power is removed and it kicks over to the battery power the transformer buzzes loudly then quiets down some but still is a hum that abnormally loudl. The greater the power draw, the quieter it is. Is this normal? Is this a sign that it might be going bad? Otherwise, it seems to function normally. - Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:28 AM . Last Modified: 2024-03-11 02:35 AM
It's normal and remember these are support to be in server rooms so you would not hear it anyway over the other servers
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:28 AM . Last Modified: 2024-03-11 02:36 AM
Hi,
thank you for your question.
I also think about that problem some days ago.
I will try to give some answers from my point of view.
- Yes, it is very loud noise, for example 50 to 55 dB (A)
- Yes, this kind of UPS for example Rack Mount UPS are for Server Rooms with Racks in it
But, what exactly is the source of that loudness?
Some background
- If you have an Online UPS the AC Voltage is "changed" into DC voltage.
- With this DC voltage the Battery is always loaded
- And further the voltage from the Battery is "changed" into AC voltage which is given to Server, Workstations and other equipment
A Try to answer the question
- Such UPS has some Switched-Mode Power Supply. They use NOT a frequency of lets say 50Hz but they use much higher frequency, for example 20 kHz.
- Also such UPS has an Inverter. You need this to chop the DC voltage from the Battery to "create" AC voltage.
- Also there are a lot of electronic devices.
- All this together but especially the inverter makes this noice.
Message was edited by: Magnussen
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:28 AM . Last Modified: 2024-03-11 02:35 AM
It's normal and remember these are support to be in server rooms so you would not hear it anyway over the other servers
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.