APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:07 AM . Last Modified: 2024-02-29 10:52 PM
After recently upgrading all our UPS Mangment cards on site to v6.2.1 , we seem to have a problem where all of the managment cards stop responding to pings all at once (nothing in the logs indicate what is happening) before comming back up what seems to be a minute later. Normally this would not be a big deal except we get paged everytime a UPS goes down.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:07 AM . Last Modified: 2024-02-29 10:52 PM
Hi Kurt,
Thanks, here is my updated feedback:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:07 AM . Last Modified: 2024-02-29 10:52 PM
Hi Kurt,
Here is what went through my mind to narrow it down:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:07 AM . Last Modified: 2024-02-29 10:52 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:07 AM . Last Modified: 2024-02-29 10:52 PM
Hi Kurt,
Thanks, here is my updated feedback:
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.