Hello,
I have a SmartUPS 30kVA and 3 power sources (1 mains, 1 500kVA day generator and 1 45kVA night generator). To comand the changeover i have 2 automatic transfer switchs.
The UPS was installed 1 week ago and after a changeover it goes to bypass mode with the information In bypass in response to an internal hardware fault.
After i restart the UPS it works fine.
Some useful information:
About UPS | |
Model: | Smart-UPS VT 30 kVA |
Serial Number: | PS1536230382 |
Firmware Revision: | 909.0718.I |
Manufacture Date: | 09/03/15 |
Status | |||
Last Battery Transfer: | Due to software command or UPS's test control | ||
Internal Temperature: | 30.0°C | ||
Runtime Remaining: | 27hr 11min | ||
Power | Phase L1 | Phase L2 | Phase L3 |
Input Voltage: | 215.0 VAC | 215.6 VAC | 216.3 VAC |
Bypass Input Voltage: | 215.9 VAC | 214.9 VAC | 216.0 VAC |
Output Voltage: | 219.7 VAC | 219.1 VAC | 219.3 VAC |
Current: | 00.00 Amps | 00.00 Amps | 00.00 Amps |
Input Frequency: | 50.02 Hz | ||
Load | Phase L1 | Phase L2 | Phase L3 |
Output Load: | 000.3 kVA | 000.1 kVA | 000.0 kVA |
Output Percent Load: | 003 %kVA | 001 %kVA | 000 %kVA |
Output Percent Power: | 002 %Watts | 000 %Watts | 000 %Watts |
Output Current: | 0001 Amps | 0000 Amps | 0000 Amps |
Output Frequency: | 50.21 Hz | ||
Battery | |||
Capacity: | 98.7 % | ||
Nominal Battery Voltage: | 192.0 VDC | ||
Actual Battery Bus Voltage: | 202.6 VDC | ||
Battery Current: | -0001.0 Amps | ||
External Battery Cabinet Rating: | 0000 | ||
Batteries: | 12 | ||
Bad Batteries: | 0 | ||
Intelligence Module | |||
Firmware Revision: | 07.18 | ||
Serial Number: | PS1536230382 | ||
Manufacture Date: | 09/03/15 | ||
Hardware Revision: | 1 |
m state: 09 02 02 02000038 00000000 00000001 03
Can someone help me?
Thanks
Nelson
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:14 AM . Last Modified: 2024-03-18 03:40 AM
Hi jon,
Thanks for the fast response.
Unfortunately im in africa and i can't contact the number ou gave me. Is there any international number? Or something i can do to try and diagnose what's wrong with my ups?
Thanks
Nelson
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:14 AM . Last Modified: 2024-03-18 03:40 AM
Hi jon,
Thanks for the fast response.
Unfortunately im in africa and i can't contact the number ou gave me. Is there any international number? Or something i can do to try and diagnose what's wrong with my ups?
Thanks
Nelson
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.