APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 1 month ago
Hello
We do have a Smart-UPS RT 5000 XL plus a extra battery pack installed in production.
After haveing couple outages, we noticed that the battery runtime of about an hour is not enough for the worst case.
Anyhow we bought a generator.
The UPS is not accepting the power of the generator.
We looked at the waveform, its a quite a good sine wave with some small hickups. (inverter Gen)
Frequency and Voltage is stable.
The UPS tries to switch to utility power and immidiately switches back to battery.
The Logs say continously :
08/07/2015 | 14:00:23 | UPS: On battery power in response to rapid change of input. |
08/07/2015 | 14:00:23 | UPS: No longer on battery power. |
As far as i understood the UPS should be able to utilize the gnerator power and do double conversation.
Occasionally the UPS switches to battery for few seconds even when on grid power, i guess caused small fluctuations in the grid.
Any idea how we can ajust the sensivity?
The generator output is 3 times larger than the load on the UPS.
Any help is appreaciated.
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:23 PM . Last Modified: 1 month ago
Thanks for getting those ready. I will follow up again with local escalation support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 1 month ago
Do you have a scope output you can share? This is tough to argue without seeing that or maybe having someone on our side review it because it appears fine from what you have reviewed but apparently the UPS is seeing a problem with it. Online UPSs don't have a sensitivity setting like standby or line interactive models because of their topology to begin with.. They allow such a wide range of voltage on the input since they are recreating the sinewave on the output. If the UPS is seeing a problem, it must be fairly severe to cause it to run on battery.
Some causes could be voltage, frequency (both you mentioned), electrical noise, change in voltage over time, etc. So, maybe it is not something super obvious that the scope reading may show when zooming in.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 1 month ago
Hi Angela,
Sorry for the delay, we had to wait for a good time to run the generator.
For what we are seeing the UPS should accept the Input. See Link below.
https://www.youtube.com/watch?v=bIyjBtQO2O0&feature=youtu.be
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 1 month ago
Thanks for sharing the video. Let me ask one of our UPS experts and see what he thinks. Hope to respond early next week.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 1 month ago
Hi Angela,
Any word from the UPS Expert?
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:22 PM . Last Modified: 1 month ago
Hi Amita,
Sorry, I contacted your local expert and I thought he said he was escalating it within CCC and overseeing the case. Have you heard anything from EMEA/local technical support? If not, I'll follow up with them.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:23 PM . Last Modified: 1 month ago
Hi Angela,
Thanks for the quick response, no nobody had contacted me yet.
That would be great if you could follow up on that.
Thanks in advance!
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:23 PM . Last Modified: 1 month ago
Hi Amita,
I apologize, I think I confused your video with another forum post here but I clarified it with myself now My fault for the delay.
Can you get your full NMC logs available and ready (event.txt, data.txt, and config.ini or the .tar file if v6 firmware)? Instructions here -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA156131
I will still see if local tech support can contact you to further look at that scope video and discuss.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:23 PM . Last Modified: 1 month ago
Thanks, i have the files ready.
Waiting then until someone contacts me.
Thanks for your help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:23 PM . Last Modified: 1 month ago
Thanks for getting those ready. I will follow up again with local escalation support.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.