APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
Hi,
My Smart-UPS 1500 (sua1500rmi2u) has 3 orange and 2 red leds blinking (without beeps or sound).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
Hi Salvatore,
As to what Bill has posted before, if the LEDs won't go back to normal after following the steps that he has recommended and it is still producing the same behavior then the UPS should now be replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
Is the sentitivy set to High Or Med?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
On 10/29/2016 6:45 PM, john said:Is the sentitivy set to High Or Med?
It was High. I already try to set it to medium but the problem persists.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
I've been able to solve some weird behaviours by disconnecting the ups from supply and then disconnect the battery. Wait some minutes and then reconnect the battery and plug into mains.
Hope it'll help
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
On 10/29/2016 10:37 PM, Valerio said:I've been able to solve some weird behaviours by disconnecting the ups from supply and then disconnect the battery. Wait some minutes and then reconnect the battery and plug into mains.
Hope it'll help
I'll will try tomorrow.
Shutdown the UPS, disconnect from power and again press 0 to disconnect Battery power doesn't work. I'll try to disconnect the battery.
It's strange that all works and Powerchute reports that everything works. But leds are blinking...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
On 10/29/2016 10:37 PM, Valerio said:I've been able to solve some weird behaviours by disconnecting the ups from supply and then disconnect the battery. Wait some minutes and then reconnect the battery and plug into mains.
Hope it'll help
i tried to disconnect the battery but leds are blinking yet.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
Hi,
Try this reset procedure
1) Turn off and unplug UPS from wall
2) Press and hold the OFF button again
3) You may see a quick flash of the LED's and you should hear an audible "click" from the UPS.
4) Plug UPS back into the wall and turn UPS back on
If this does not resolve the issue then there is an internal fault and the UPS will need to be replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
On 10/31/2016 2:06 PM, Bill said:Hi,
Try this reset procedure
1) Turn off and unplug UPS from wall
2) Press and hold the OFF button again
3) You may see a quick flash of the LED's and you should hear an audible "click" from the UPS.
4) Plug UPS back into the wall and turn UPS back onIf this does not resolve the issue then there is an internal fault and the UPS will need to be replaced.
after procedure leds are blinking yet. But why powerchute reports that's all fine and all work fine? Thanks in advance.
S.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
You just did a question that any answer this is usable by a very experienced electronics engineer and also specialist in electronics repairs.
Sort explanation this is inside components aging issues including capacitors and electrical relay.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 3 weeks ago
Hi Salvatore,
As to what Bill has posted before, if the LEDs won't go back to normal after following the steps that he has recommended and it is still producing the same behavior then the UPS should now be replaced.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.