Posted: 2021-06-30 08:53 PM . Last Modified: 2 weeks ago
Hi All,
Im looking at getting an APC UPS ( APC SUA1000RM1U Smart-UPS 1000VA USB & SERIAL RM 1U 230V #A4 perhaps) to buy sometime to have critical gear shutdown during power outages. Equipment such as Main PC, NAS & DVR.
It needs to be automated so it can occur if Im not home or asleep. Can this be done & what is the best way to achieve this?
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:53 PM . Last Modified: 2 weeks ago
The exact answer depends upon the equipment you have. The PC can definitely be made to shut down automatically if needed. It's the DVR and NAS that are more of a question, and it would help to know more about them.
It is possible for a single UPS to signal multiple computers and let them know that they need to shut down. APC has solutions to support this, and there are third party options (such as Network UPS Tools or apcupsd) available as well.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:53 PM . Last Modified: 2 weeks ago
HOW TO REMOTE SHUTDOWN ALL MACHINES (PC and MAC) ATTACHED TO AN APC UPS
To remotely shutdown any PC on the same network:
CHANGE THE FOLLOWING SETTINGS ON EACH REMOTE COMPUTER:
In CONTROL PANEL
Network and Sharing Center, Change Advanced Sharing settings
"Private" enable "Turn on File and Printer sharing"
In REGEDIT
RUN regedit.exe
Add a new DWORD
HKEY_LOCAL_MACHINE\SOFTWARE\Microsoft\Windows\CurrentVersion\Policies\System
LocalAccountTokenFilterPolicy DWORD:00000001
In SECPOL (Windows Pro and Enterprise ONLY)
RUN secpol.msc
Local Security Policy, Security Settings, Local Policies, User Rights Assignment
Add "Everyone" to "Force shutdown from a remote system"
Then set up the event task in TASK SCHEDULER from the PC with the UPS attached to it.
RUN taskschd.msc
TO SHUTDOWN ALL NOMINATED MACHINES
CREATE BASIC TASK
Give the TASK a NAME and a DESCRIPTION [next]
Trigger: “When a specific event is logged” [next]
When an event is logged:
LOG: Application
SOURCE: APC UPS SERVICE
EVENT ID: 174
[next]
ACTION: “Start a program” [next]
START A PROGRAM
c:\scripts\upsshutdown.bat [next]
[finish]
TO CANCEL SHUTDOWN OF ALL NOMINATED MACHINES
CREATE BASIC TASK
Give the TASK a NAME and a DESCRIPTION [next]
Trigger: “When a specific event is logged” [next]
When an event is logged:
LOG: Application
SOURCE: APC UPS SERVICE
EVENT ID: 61455
[next]
ACTION: “Start a program” [next]
START A PROGRAM
c:\scripts\upscancelshutdown.bat [next]
[finish]
BATCH FILES (to be added to c:\scripts\)
upsshutdown.bat
shutdown /s /m \\computer_name /t 120 /c “AC BLACKOUT - ORDERED SHUTDOWN IN PROGRESS”
add one line per PC you want to shutdown.
upscancelshutdown.bat
shutdown /a /m \\computer_name
add one line per PC you want to cancel the shutdown process
END OF PC METHOD
To remotely shutdown any MAC on the same network
Make sure the mac is visible on the PC with the UPS attached to it and the MAC user area is shared.
edit the ups shutdown.bat file and add the following lines for each MAC you want to shut down.
net use x: \\MAC-NAME\username
del x:\shutdown.txt
echo shutdown > x:\shutdown.txt
net use x: /delete
On each MAC
Open Automator (applications -> automator)
Choose “Folder Action” and click “choose”
Click the “Choose folder” dialog box, select “other” and select the default user folder that corresponds to \\MAC-NAME\username and click “choose”
In “Library -> utilities” select “Run AppleScript” and drag the action into the right hand panel
replace the default AppleScript with the following:
on run {input, parameters}
tell application "Finder"
if exists POSIX file "/users/timstevenson/shutdown.txt" then
say "There has been a power cut. I'm going to shutdown in one minute."
delay 60
tell application "System Events"
set ProcNm_ to name of every application process whose visible is true
repeat with i_ from 1 to count items of ProcNm_
set TarProc_ to item i_ of ProcNm_
try
tell application TarProc_ to quit
end try
end repeat
repeat with i_ from 1 to count items of ProcNm_
set TarProc_ to item i_ of ProcNm_
try
if TarProc_ does not equal "Finder" then set app_name to TarProc_
set the_pid to (do shell script "ps ax | grep " & (quoted form of app_name) & " | grep -v grep | awk '{print $1}'")
if the_pid is not "" then do shell script ("kill -9 " & the_pid)
end try
end repeat
tell application "finder" to shut down
end tell
end if
end tell
return input
end run
SAVE the Automator file as UPSShutdown
END OF MAC METHOD
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:53 PM . Last Modified: 2 weeks ago
Not sure what the DVR will be yet, depends on what I can get. It may in fact be an NVR.
The NAS is a QNAP TS-419+.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:53 PM . Last Modified: 2 weeks ago
Thanks Tim.