I have two servers who are connected to two different APC Smart-ups. Problem that I have is that neither server starts automatically after power restore when a power failure has happen.
Can someone tell me what I am doing wrong that the servers does not start automatically after power restore?
Servers |
Connected to UPS |
HP Proliant ML370 G5 |
APC Smart-UPS 2200 |
HP Proliant ML350p Gen8 |
APC Smart-UPS 1500 |
Basic settings both UPS |
|
Time required for shutdown sequence |
12 minutes |
Low battery signal |
8 minutes |
OS shutdown duration |
10:30 minutes |
OS shutdown type |
shutdown |
Enable OS reboot |
Yes |
UPS turn on battery capacity |
30% |
UPS turn on delay |
1 minutes |
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:49 PM . Last Modified: 2024-03-06 10:37 PM
Hi,
You need to set OS to turn on when AC is restored in the BIOS of the computers. We have Kbase FA159550 "Computer will not automatically reboot after UPS has shutdown and restarted" that should help with this issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:49 PM . Last Modified: 2024-03-06 10:37 PM
Hi,
You need to set OS to turn on when AC is restored in the BIOS of the computers. We have Kbase FA159550 "Computer will not automatically reboot after UPS has shutdown and restarted" that should help with this issue.