SURTD5000RMXLP3U on-battery no-load watts amps?
Looking for the DC amp draw for a SURTD5000RMXLP3U, on-battery, no-load. Uses RBC140s, 2 sleds, 96v each, 192v total. Prefer measurables, not estimates. Our DC clamp amp meter went bad, waiting on a replacement. Trying to build XL requirements, we've measured the devices, would prefer to know static amps, so we can do the math, for possible extra batteries, pre-gen-set activation.
Other thread states "Based on the online thermal dissipation value listed of 1589 and knowing 1 watt = 3.41BTU, that gives me about ~466 watts you could expect worst case.". That sounds to be 2.43a @ 192v, yet would prefer measurables.