APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:28 AM . Last Modified: 2 weeks ago
Hello everyone,
I need to ask you about a certain installation at a customer's site.
We have 8 UPS's SURT10000XLI installed for Pharmaceutical Laboratory single phase equipment.
For some redundancy reasons, all of the UPS's inputs are supplied from a larger 80 KVA three phase UPS system.
Lately we have faced some problems with 3 out of 8 ups's, one by one. The inverter was defected, and showed an error code 00100.
Could this installation, of one large ups supplying 8 smaller ups, be causing any degradation of power quality, and by that having an impact on the ups's inverter board components?
Thanks in advance for any insight you have for me.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:28 AM . Last Modified: 2 weeks ago
Where did you see inverter fault reported? I see 00100 as a PFC failure. What is the load attached to the UPS or does this occur with no attached load?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:28 AM . Last Modified: 2 weeks ago
Where did you see inverter fault reported? I see 00100 as a PFC failure. What is the load attached to the UPS or does this occur with no attached load?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.