APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:43 PM . Last Modified: 3 weeks ago
I replaced the batteries in a SUA1000XL and the SUA24XLBP and moved the UPS to a new location. The AP9631 shows Load Power of 72.8% watts, 66.3% VA, load current of 5.4 amps and Runtime remaining of 38 minutes (with one external battery configured.) I set the Last Battery replacement to January 2016.
I calculated the watts as .728*800=582.4.
The APC Runtime graph for a SUA1000XL and one battery pack shows 98.4 minutes with a load of 585 watts...yet the NIC is showing only 38 minutes. Is this because the UPS is still using a previous run time calibration? Is there anyway short of performing a Runtime calibration to force the NIC/UPS to show an updated run time?
Thanks,
Jeff
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:43 PM . Last Modified: 3 weeks ago
Or is the difference between the APC graph and what the NIC is showing due to the power factor (VA versus Watts) not being 1.0?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:43 PM . Last Modified: 3 weeks ago
Or is the difference between the APC graph and what the NIC is showing due to the power factor (VA versus Watts) not being 1.0?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.