Posted: 2021-06-30 10:43 PM . Last Modified: 2024-03-06 10:42 PM
A few days ago, I had a battery alarm on one of my SMT2200RM2U, and the device ended up shutting down on me. I went ahead and ordered a new battery for it, and it just arrived this morning. I have installed the battery, and powered the device back on, however once it powers on it shows NO AC on the LCD display, and when I try to run a self test, it shows that it is only available in Online mode. So now I am wondering if the old battery was in fact not bad, and if there is something wrong with the device itself? Any suggestions/recommendations?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:43 PM . Last Modified: 2024-03-06 10:42 PM
Hi Brian,
If the unit is saying there is no AC that means it is not seeing utility power coming from the wall outlet it is plugged into. Can you try a different circuit or perhaps use a volt meter to measure the voltage coming from the outlet to confirm we have power. Perhaps a breaker was tripped on the outlet. If we confirm we have good utility power and the unit continues to not see it (check the status menu and the V in reading. It should be about 120volts), there might be a problem with something internal to the unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:43 PM . Last Modified: 2024-03-06 10:42 PM
Hi Brian,
If the unit is saying there is no AC that means it is not seeing utility power coming from the wall outlet it is plugged into. Can you try a different circuit or perhaps use a volt meter to measure the voltage coming from the outlet to confirm we have power. Perhaps a breaker was tripped on the outlet. If we confirm we have good utility power and the unit continues to not see it (check the status menu and the V in reading. It should be about 120volts), there might be a problem with something internal to the unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:43 PM . Last Modified: 2024-03-06 10:42 PM
Thanks. I have checked all breakers, and tried a few other outlets, but the result is the same. I went and looked at the status, and the Input is at 141.09V. I'm beginning to think that the unit may be bad.
One more thing I want to mention, is that while browsing through the menus, I saw that Output was Off.
Thanks,
Brian
Link copied. Please paste this link to share this article on your social media post.