The SC-1500 uses 4 cells (2 inverted over two). It seemed easy enough pulling it apart, but now that I have fresh batteries......I need some assistance with the wiring.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:20 AM . Last Modified: 2024-03-12 11:42 PM
Factory replacement battery module is an RBC59... I googled that but there are no "exploded diagram". The batteries are wired as two series strings connected in parallel.
( on main batt connector) --- [ batt 1 ] --- [batt2] ---------- ( on main batt connector)
\ /
\- [ batt3] --- [batt4] ---/
hope this diagram comes thru ok.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:20 AM . Last Modified: 2024-03-12 11:42 PM
Factory replacement battery module is an RBC59... I googled that but there are no "exploded diagram". The batteries are wired as two series strings connected in parallel.
( on main batt connector) --- [ batt 1 ] --- [batt2] ---------- ( on main batt connector)
\ /
\- [ batt3] --- [batt4] ---/
hope this diagram comes thru ok.