APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:03 AM
hello
How to get Runtime Calibration test result. Please help me
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:02 AM
When you run a Runtime Calibration you are calibrating the load the available battery/s. The runtime calibration results are posted to the available runtime. Below is a screenshot from a Smart-UPS 700 that shows the runtime at 6 minutes. If I run a Runtime Calibration if there is a change it would be posted here.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:02 AM
When you run a Runtime Calibration you are calibrating the load the available battery/s. The runtime calibration results are posted to the available runtime. Below is a screenshot from a Smart-UPS 700 that shows the runtime at 6 minutes. If I run a Runtime Calibration if there is a change it would be posted here.