Good Day,
I have AP9619 but I can't remember an IP address. May I have the steps of how to reset to default?
Best Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:18 AM . Last Modified: 2024-02-29 11:20 PM
Hi,
In order to reset AP9619 to default, you need to log into it somehow. If you can't get to it remotely because you forgot/lost the IP, then you'll need to serial into it.
Instructions to do that are here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156075
Instructions to assign an IP are here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156064
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:18 AM . Last Modified: 2024-02-29 11:20 PM
Hi,
In order to reset AP9619 to default, you need to log into it somehow. If you can't get to it remotely because you forgot/lost the IP, then you'll need to serial into it.
Instructions to do that are here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156075
Instructions to assign an IP are here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156064