You should not use the Advanced UPS configuration. Install the PowerChute appliance on an ESXi host at each site. Configure PowerChute to migrate the VMs. Within PowerChute you are given the option of migrating to any available host, or to specify a host, or hosts. Each PowerChute appliance will listen to the UPS at its site. When the UPS switches to battery it will migrate to the available ESXi hosts if the host/s are compatible. It will the power off any remaining VMs, and then the host/s.
If the Datacore servers are not powered off, you may need to write an SSH script that PowerChute will run before or after the host/s have powered off. You can also write one the PowerChute will run after the host power on to bring the Datacore server back online.