APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:24 AM . Last Modified: 2024-03-13 05:37 AM
We replaced a dead (malfunctioning) UPS yesterday with a Smart-UPS 3000 RM XL, and started apcupsd to monitor it about 7PM yesterday (It was powered up in the morning). Currently there is no load on the UPS. Today apcupsd started reporting near continual Self Tests.
I just tried APC's chat line, but they're not in the office today.
I was hoping someone here might be able to give suggestions as to what is happening.
I'm hoping there's a way to recover from this and that the UPS is not DOA.
Status at first test this morning:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:24 AM . Last Modified: 2024-03-13 05:37 AM
yes, i agree. it was probably an older, faulty serial cable. we have seen this before.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:24 AM . Last Modified: 2024-03-13 05:37 AM
This apparently turned out to be a serial cable problem. We continued to use the previous cable (940-1524C) rather than the one that came with the new UPS (940-0024E).
Apparently the wrong cable worked ok initially. It seems like it behaved differently when the UPS decided to do a Self Test.
Some of the symptoms:
1. When I got to the UPS, it was on the battery. The online light was off. After a while, the online light would come back on and blink about 20 times before turning off again.
2. When I tried to turn off the UPS by holding in the power button, it would start back up when I released the button.
When I unplugged the 940-1524C cable, the UPS showed the online light and was no longer on the battery. When I plugged in the 940-0024E cable, everything seemed to work. Of course, there could still be another problem that shows up the next time it does a Self Test.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:24 AM . Last Modified: 2024-03-13 05:37 AM
yes, i agree. it was probably an older, faulty serial cable. we have seen this before.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.